What is the minimum feeder demand for twelve single-phase 12 kW ranges supplied by a 3-phase, 4-wire 120/208 V feeder?

Study for the Independent Electrical Contractors (IEC) Year 4 Test. Use flashcards and multiple-choice questions, each with hints and explanations. Prepare effectively for your exam!

Multiple Choice

What is the minimum feeder demand for twelve single-phase 12 kW ranges supplied by a 3-phase, 4-wire 120/208 V feeder?

Explanation:
In a 3-phase, 4-wire 120/208 V system, you don’t size the feeder for every single watt of every single-phase load. When many single-phase appliances are spread across the three phase pairs, the loads can be balanced so the feeder current is much less than the simple sum of all watts. That balancing is accounted for with a demand factor for multiple single‑phase loads on a 3-phase feeder. For twelve identical single-phase loads, each 12 kW, the total connected load is 12 × 12 = 144 kW. The practical minimum feeder demand on a 3-phase feeder with balanced single-phase loads is obtained by distributing the loads across the three phase paths, which yields a factor around 1/6 of the total. 144 kW divided by 6 gives 24 kW. Because this system is 120/208 V, the standard rounding and voltage considerations bring the value down slightly, so the accepted minimum feeder demand comes out to about 23 kW. So the minimum feeder demand for this setup is around 23 kW, which matches the stated correct choice.

In a 3-phase, 4-wire 120/208 V system, you don’t size the feeder for every single watt of every single-phase load. When many single-phase appliances are spread across the three phase pairs, the loads can be balanced so the feeder current is much less than the simple sum of all watts. That balancing is accounted for with a demand factor for multiple single‑phase loads on a 3-phase feeder.

For twelve identical single-phase loads, each 12 kW, the total connected load is 12 × 12 = 144 kW. The practical minimum feeder demand on a 3-phase feeder with balanced single-phase loads is obtained by distributing the loads across the three phase paths, which yields a factor around 1/6 of the total. 144 kW divided by 6 gives 24 kW. Because this system is 120/208 V, the standard rounding and voltage considerations bring the value down slightly, so the accepted minimum feeder demand comes out to about 23 kW.

So the minimum feeder demand for this setup is around 23 kW, which matches the stated correct choice.

Subscribe

Get the latest from Examzify

You can unsubscribe at any time. Read our privacy policy