What is the minimum general lighting load for a 11,000 sq-ft courthouse?

Study for the Independent Electrical Contractors (IEC) Year 4 Test. Use flashcards and multiple-choice questions, each with hints and explanations. Prepare effectively for your exam!

Multiple Choice

What is the minimum general lighting load for a 11,000 sq-ft courthouse?

Explanation:
The essential idea is to size the minimum general lighting load using the occupancy’s per-square-foot rating and the total area. For a courthouse, the NEC provides a general lighting load factor of 1.4 VA per square foot. Multiply by the area: 11,000 ft² × 1.4 VA/ft² = 15,400 VA. This 15,400 VA is the minimum lighting load used for service sizing, not the exact installed load. Other values would correspond to different per-square-foot factors (e.g., 3.0 VA/ft² for some office-type spaces) and don’t match the courthouse rating.

The essential idea is to size the minimum general lighting load using the occupancy’s per-square-foot rating and the total area. For a courthouse, the NEC provides a general lighting load factor of 1.4 VA per square foot. Multiply by the area: 11,000 ft² × 1.4 VA/ft² = 15,400 VA. This 15,400 VA is the minimum lighting load used for service sizing, not the exact installed load. Other values would correspond to different per-square-foot factors (e.g., 3.0 VA/ft² for some office-type spaces) and don’t match the courthouse rating.